Where do i put a service switch, if any, for 12hp fire pump. Fire pump is installed on the 12th floor with MCA-75-20 controller. Controller has a built-in isolating switch.
I think the disconnecting means need only to carry 115% of the motor running amperes, be rated for the horsepower, and have OC protection that will carry LR current.If one is installed it has to be able to carry locked rotor current.
I agree but OCPD means overcurrent protective device and a disconnecting means is not an OCPD. Notice that I said, ". . . and have OC protection that will carry LR current." Sorry, Tom, I think I gotcha.See 695.4(1) OCPD shall carry locked rotor current indefinitely