I hope some of you can clear something up for me.
2008 NEC 695 is very clear that a fire pump should run in the event of a fire until the fire is out or the pump itself is destroyed.
If you use an overcurrent device between the power source and the fire pump controller, it must be sized to locked-rotor current and comply with 695.4
NEC 695.6: "power circuits and wiring methods shall comply with the requirements in 695.6(A) thru (H)." 695.6(D) Overcurrent Protection: "power circuits shall not have automatic protection against overloads. Except for protection of transformer primaries provided in 695.5(C)(2), branch-circuit and feeder conductors shall be protected against short circuit only."
Is 695.6(D) rule stating that short-circuit protection is required at the power source or is it requiring short-circuit protection on the load side at the fire pump controller?
thank you so much for the clarification
Errol
2008 NEC 695 is very clear that a fire pump should run in the event of a fire until the fire is out or the pump itself is destroyed.
If you use an overcurrent device between the power source and the fire pump controller, it must be sized to locked-rotor current and comply with 695.4
NEC 695.6: "power circuits and wiring methods shall comply with the requirements in 695.6(A) thru (H)." 695.6(D) Overcurrent Protection: "power circuits shall not have automatic protection against overloads. Except for protection of transformer primaries provided in 695.5(C)(2), branch-circuit and feeder conductors shall be protected against short circuit only."
Is 695.6(D) rule stating that short-circuit protection is required at the power source or is it requiring short-circuit protection on the load side at the fire pump controller?
thank you so much for the clarification