D douglas11 Member Oct 16, 2012 #1 like to know if the fire pump disconnect means from the generator has to be sized to locked rotor of the fire pump,thanks
like to know if the fire pump disconnect means from the generator has to be sized to locked rotor of the fire pump,thanks
A anbm Senior Member Location TX Occupation Designer Oct 17, 2012 #2 If the generator is the primary power source, yes. If the generator is the backup power source, no.