hhsting
Senior Member
- Location
- Glen bunie, md, us
- Occupation
- Junior plan reviewer
I have odd situation. Incoming FEEDER is feeding 480/277V switchgear 2000 amps with main breaker of 2000 amps. On the line side of the 2000 amps main breaker I have a tap and this tap would be feeder tap since incoming conductors are feeders not service conductors. The tap is feeding fire pump approximately 100 feet away that has disconnecting means and fire pump controller.
Now the question becomes since these are feeder taps one disconnecting means needs to be provided with overcurrent protection within 25 feet. However, NEC 2014 695.4(B)(1) says one disconnecting means shall be provided with overcurrent protection devices shall be permitted installed between fire pump power sources and fire pump controller. Also I don't see NEC 2014 695.3(A) fire pump shall be fed by feeder taps. Is their anything in NEC 2014 that would not allow me to feeder tap fire pumps?
Now the question becomes since these are feeder taps one disconnecting means needs to be provided with overcurrent protection within 25 feet. However, NEC 2014 695.4(B)(1) says one disconnecting means shall be provided with overcurrent protection devices shall be permitted installed between fire pump power sources and fire pump controller. Also I don't see NEC 2014 695.3(A) fire pump shall be fed by feeder taps. Is their anything in NEC 2014 that would not allow me to feeder tap fire pumps?