695.6(2) Feeders. Fire pump supply conductors on the load side of
the final disconnecting means and overcurrent device(s)
permitted by 695.4(B), or conductors that connect directly to
an on-site standby generator, shall comply with all of the following:
(a) Independent Routing. The conductors shall be kept
entirely independent of all other wiring.
(b) Associated Fire Pump Loads. The conductors shall
supply only loads that are directly associated with the fire pump
system.
(c) Protection from Potential Damage. The conductors shall
be protected from potential damage by fire, structural failure,
or operational accident.
(d) Inside of a Building. Where routed through a building,
the conductors shall be protected from fire for 2 hours
using one of the following methods:
(1) The cable or raceway is encased in a minimum 50 mm
(2 in.) of concrete.
(2) The cable or raceway is a listed fire-resistive cable system.