Fire Rated Device Box Enclosure?
titan1021
I've got a job going where I have to put several receptacle boxes in a fire wall and was hoping to find some kind of fire rated enclosure for device boxes to save the trouble of having to box each one in with drywall. I have no problem finding them for cans and ceiling lights, but nothing for walls.
Anyone know if they exist?
Thanks
the normal wall boxes are fire rated plus you can add fire putty pads around the boxes. what is the wall rating in hours?
Most regular boxes are fire-rated, as long as you limit the opening size and opening spacing.
This might help:
Metallic Outlet Boxes (QCIT) for use in fire-resistant rated assemblies All UL Listed single- and double-gang metallic outlet and switch boxes with metallic or nonmetallic cover plates may be installed in bearing and nonbearing wood stud and steel stud walls with fire rating not exceeding 2 hours. These metallic boxes
are not required to be marked specifically as suitable for use in fire-resistant rated assemblies. Metallic boxes located on opposite sides of walls or partitions
are intended to be separated by a minimum horizontal distance of 24 in.
This minimum separation distance between boxes may be reduced when Wall Opening Protective Materials (QCSN) (commonly known as putty pads) are installed according to the requirements of their Classification. Putty pads other than those installed on the outer surfaces of a metallic box prior to installation of the wall are also available. UL Classified putty pads, also known in industry as box inserts, are for installation on the inside back surface of the box. There are also putty pads, known in industry as gaskets, available for application under the wiring device cover plate.