Our state follows the 2023 version of the NEC. We need to 2-hour rate our emergency feeders. Here is the relevant code section on doing so, from our version of 700.10(D):
Feeder-circuit wiring shall meet one of the following conditions:
If we run the feeder outside of the building, can the building itself be considered a listed fire-rated assembly? As in, can we simply run regular EMT and conductors outside of the building? For various reasons, we cannot run inside the building. The building is mostly masonry block for the exterior.
(1) Feeder-Circuit Wiring
Feeder-circuit wiring shall meet one of the following conditions:
- The cable or raceway is installed in spaces or areas that are fully protected by an approved automatic fire protection system.
- The cable or raceway is protected by a listed electrical circuit protective system with a minimum 2-hour fire rating.
Informational Note No. 1: See UL 1724, Fire Tests for Electrical Circuit Protection Systems, for one method of defining an electrical circuit protective system. The UL Guide Information for Electrical Circuit Integrity Systems (FHIT) contains information to identify the system and its installation limitations to maintain a minimum 2-hour fire-resistive rating and is available from the certification body. - The cable or raceway is a listed fire-resistive cable system with a minimum 2-hour fire rating.
Informational Note No. 2: See UL 2196-2017, Standard for Fire Test for Circuit Integrity of Fire-Resistive Power, Instrumentation, Control and Data Cables, for one method of defining a fire-resistive cable system. - The cable or raceway is protected by a listed fire-rated assembly that has a minimum fire rating of 2 hours and contains only emergency circuits.
- The cable or raceway is encased in a minimum of 50 mm (2 in.) of concrete.
If we run the feeder outside of the building, can the building itself be considered a listed fire-rated assembly? As in, can we simply run regular EMT and conductors outside of the building? For various reasons, we cannot run inside the building. The building is mostly masonry block for the exterior.