Fire Rated - Fire Pump cable

Status
Not open for further replies.

Mostafa Noah

Member
Location
Cairo, Egypt
Greetings,
I apologize if this question is repeated, the cables feeding the electrica fire pump control panel coming from two different sources are installed inside a concerte duct bank, shall we specify this feeders as a Fire rated cables ?, if no, please provide me with the quotation from NFPA
 
IMO you'r done without the fire rated cables based on 700.10(d)(1)(5) as long as the fire cable be encased in a minimum of 50 mm (2 in.) of concrete.
 
Greetings,
I apologize if this question is repeated, the cables feeding the electrica fire pump control panel coming from two different sources are installed inside a concerte duct bank, shall we specify this feeders as a Fire rated cables ?, if no, please provide me with the quotation from NFPA
Well I wont quote what the other reply stated, I will just tell you that in accordance with 695.6(A)(2)(1) should have you covered. You would not need to call it anything other than what it is, fire pump supply conductors being installed in accordance with the code section mentioned above. [695.6(A)(2)(1)]
 
Well I wont quote what the other reply stated, I will just tell you that in accordance with 695.6(A)(2)(1) should have you covered. You would not need to call it anything other than what it is, fire pump supply conductors being installed in accordance with the code section mentioned above. [695.6(A)(2)(1)]
Where could i find 695.6(A)(2)(1) unless it's there in NEC 2014 which i don't have otherwise you refer to 695.6(A)(2)(d) & it's just a typo, if you mean 695.6(A)(2)(D) that would say the same as 700.10(d)(1)(5).
 
Yep...typo...Should have been 695.6(A)(2)(d)(1)

Yes, it is the same but more relevant since the discussion is about fire pump feeders.
 