geochurchi
- Concord,NH
- Retired electrician
Hi, How do I treat OW boxes that have to be cut into a fire rated walls?
Thanks
Geo
Thanks
Geo
They need to be fastened directly to a framing member such as a stud. No clips are permitted to secure the box directly to the drywall.
From the UL Fire Resistance Directory
WALL AND PARTITION ASSEMBLIES
Metallic Eletrical Outlet Boxes
Listed single and double gang metallic outlet and switch boxes with metallic or nonmetalliccover plates may be used in bearing and nonbearing wood stud and steel stud walls with ratings not exceeding 2h. These walls shall have gypsum wallboard facings similar to those shown in Design Nos. U301,U411, and U425. The metallic outlet or switch boxes shall be securely fastened to the studs and the opening in the wallboard facing shall be cut so that the clearance between the box and the wallboard does not exceed 1/8 in. The surface area of individual metallic outlet or switch boxes shall not exceed 16 sq in. The aggregate surface area of the boxes shall not exceed 100 sq in per 100 sq ft of wall surface.
It's not in the NEC but you can find it in the UL Orange books.
Roger