Feeders to 36 units Residential. Floors 2 thru 4.
Service 1st floor. Is SER for 150 amp panels. Thru 2 hour rated fire slabs Acceptable.
I was going to use SER for thru floors. But Bring up a conduit from main service to the 4th floor and sleeve it down from 4th floor to Service.
EMT would be from 4 floor Ceiling cavity, Down thru 3 floors and Emt would terminate in it's respective meter slot. Can you run SER thru floors and this still have an acceptable 2 hour fire rating.
I would figure fire could go between stranded conductors at some point without EMT. Need 2 hour ratings. Just looking for some input.