I beleive this is the article that would apply from the IBC 2009. As you see there is no reference to electric rooms as such I beleive there is no such requirement.
508.2.5 Separation of incidental accessory occupancies. The incidental accessory occupancies listed in Table 508.2.5 shall be separated from the remainder of the building or equipped with an automatic fire-extinguishing system, or both, in accordance with Table 508.2.5.
Exception: Incidental accessory occupancies within and serving a dwelling unit are not required to comply with this section.
TABLE 508.2.5 INCIDENTAL ACCESSORY OCCUPANCIES
ROOM OR AREASEPARATION AND/OR PROTECTIONFurnace room where any piece of equipment is over 400,000 Btu per hour input</SPAN>1 hour or provide automatic fire-extinguishing systemRooms with boilers where the largest piece of equipment is over 15 psi and 10 horsepower</SPAN>1 hour or provide automatic fire-extinguishing systemRefrigerant machinery room</SPAN>1 hour or provide automatic sprinkler systemHydrogen cutoff rooms, not classified as Group H</SPAN>1 hour in Group B, F, M, S and U occupancies; 2 hours in Group A, E, I and R occupancies.Incinerator rooms</SPAN>2 hours and automatic sprinkler systemPaint shops, not classified as Group H, located in occupancies other than Group F</SPAN>2 hours; or 1 hour and provide automatic fire-extinguishing systemLaboratories and vocational shops, not classified as Group H, located in a Group E or I-2 occupancy</SPAN>1 hour or provide automatic fire-extinguishing systemLaundry rooms over 100 square feet</SPAN>1 hour or provide automatic fire-extinguishing systemGroup I-3 cells equipped with padded surfaces</SPAN>1 hourGroup I-2 waste and linen collection rooms</SPAN>1 hourWaste and linen collection rooms over 100 square feet</SPAN>1 hour or provide automatic fire-extinguishing systemStationary storage battery systems having a liquid electrolyte
capacity of more than 50 gallons, or a lithium-ion capacity of 1,000 pounds used for facility standby power, emergency power or uninterrupted power supplies</SPAN>1 hour in Group B, F, M, S and U occupancies; 2 hours in Group A, E, I and R occupancies.Rooms containing fire pumps in nonhigh-rise buildings</SPAN>2 hours; or 1 hour and provide automatic sprinkler system throughout the buildingRooms containing fire pumps in high-rise buildings</SPAN>2 hours
For SI: 1 square foot = 0.0929 m2, 1 pound per square inch (psi) = 6.9 kPa, 1 British thermal unit (Btu) per hour = 0.293 watts, 1 horsepower = 746 watts, 1 gallon = 3.785 L.