I need to run a new conduit from a come pad outside a bldg to a riser room control panel. It'll be underground outside. Does it need to stay underground till it reaches the controller or can I run conduit on the inside of the bldg?
 
If you mean from a utility transformer pad read 695.6(A)(1) and take note of where it sends you to 230.6(1) & (2)

Roger
 
I need to run a new conduit from a come pad outside a bldg to a riser room control panel. It'll be underground outside. Does it need to stay underground till it reaches the controller or can I run conduit on the inside of the bldg?

Unless you are talking about a fire pump feeder, it can be in conduit, or even free air within the building as a general answer. It always needs protection "where subject to damage", and insurance underwriters and certain high risk facilities may have more stringent requirements for surviveability of the system.
 
I need to run a new conduit from a come pad outside a bldg to a riser room control panel. It'll be underground outside. Does it need to stay underground till it reaches the controller or can I run conduit on the inside of the bldg?

Assuming you are referring to the supply to a fire pump, yes it will have to stay "outside" (stay underground) or use an approved 2 hr. rated wiring method until it reaches the fire pump room.
 
Assuming you are referring to the supply to a fire pump, yes it will have to stay "outside" (stay underground) or use an approved 2 hr. rated wiring method until it reaches the fire pump room.
i went by the shop and did some reading and agree.I found the same thing.

thanks
 