Re: Fire suppression - Medium Voltage Gear
Sprinkler is generally the cheapest. If you install a double interlock pre-action system, then you get the benefit of the inexpensive water with the reliability of gas release.
Double interlock pre-action requires a detector in the room to go into alarm, and a sprinkler head to fuse (reaching 165 degrees in many cases). If a head fuses elsewhere, then the switchgear room remains inactive, until called upon.
The downside of pre-action, is that if there is a fire that activates the detection and melts the 165 degree sprinkler head, and somehow wouldn't have damaged the remainder of the switchgear in that room, you'll be out of luck. But consider for a fire to melt a 165 degree sprinkler head, things are pretty bad already in this isolated room. Be sure to install curbs to reduce collateral damage in the event of an activation.