We've just experienced a fire to one of the fluorescent light fixtures and need your helps for investigation of root cause.
8 twin ligh fixtures 2x40W using magnectic ballasts are connected in parallel (so totally 16 lamps connected in paralell).
Actual measured current of a lamp branch is 0.3A.
Wire of a branch is 1mm2 solid wire, and cable of supply line is 2x4mm2 stranded wires.
One 16A inverse time MCB to switch on and off the 16 lamps.
No junction box outside the fixture for intermediate connections, in stead plastic terminal blocks are used inside light fixture for connection and jump from fixture to fixture). The terminal block and its associated wires is located about 30mm from one ballast.
Electric wires were inside the loom tubes (pls see my attachment)
At the time of the fire the 16A MCB was tripped.
Checking other fixtures we found some cases that:
The branch wire inside light fixture touched the ballast and sticked to the hot ballast since the wire sheath was melt by heat and acted as an adhesive to keep the bare core of wire in contact with the ballast case. This caused fault current of 0.7A in the branch circuit of the lamp with fault. The 0.7A did not trip 16A MCB, and monitoring of ballast iin this case showed increasing temperature.
I attach herewith the PDF file for your imagination.
Any advices on possible root cause are appriciated.
We've just experienced a fire to one of the fluorescent light fixtures and need your helps for investigation of root cause.
8 twin ligh fixtures 2x40W using magnectic ballasts are connected in parallel (so totally 16 lamps connected in paralell).
Actual measured current of a lamp branch is 0.3A.
Wire of a branch is 1mm2 solid wire, and cable of supply line is 2x4mm2 stranded wires.
One 16A inverse time MCB to switch on and off the 16 lamps.
No junction box outside the fixture for intermediate connections, in stead plastic terminal blocks are used inside light fixture for connection and jump from fixture to fixture). The terminal block and its associated wires is located about 30mm from one ballast.
Electric wires were inside the loom tubes (pls see my attachment)
At the time of the fire the 16A MCB was tripped.
Checking other fixtures we found some cases that:
The branch wire inside light fixture touched the ballast and sticked to the hot ballast since the wire sheath was melt by heat and acted as an adhesive to keep the bare core of wire in contact with the ballast case. This caused fault current of 0.7A in the branch circuit of the lamp with fault. The 0.7A did not trip 16A MCB, and monitoring of ballast iin this case showed increasing temperature.
I attach herewith the PDF file for your imagination.
Any advices on possible root cause are appriciated.