The primary local jurisdiction has always required a 4 hour rated fire wall separating occupancies in order for the the structure to be considered separate buildings allowing two services.
A new occupancy addition is being built to an existing building in a different jurisdiction and the building inspector states since it is a Class 5 construction he only requires a two hour fire wall to consider it a separate building.
Having not dealt with building codes I have always thought the 4 hr wall was a requirement. Cans some of you with knowledge of the requirement enlighten me.
 

ramsy

Roger Ruhle dba NoFixNoPay
Location
LA basin, CA
Occupation
Service Electrician 2020 NEC
Never heard of a 4-hour fire rating requirement, I thought 2 hours was the standard.
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
Never heard of a 4-hour fire rating requirement, I thought 2 hours was the standard.
The 2-hour separation allows you to consider each space separately for fire protection purposes. Otherwise, if you have adjacent occupancies, all of them have to follow the requirements of the most restrictive occupancy. For example, an educational occupancy requires a voice evacuation system. A business occupancy may require no fire alarm at all. If they are separated by a 1-hour firewall, the business occupancy now needs a voice evac system that is common with the educational occupancy.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
(revised wording of OP)
For the application of 230.2 can a separate service be installed if there is only a 2 hr wall between occupancies ??
 

ramsy

Roger Ruhle dba NoFixNoPay
Location
LA basin, CA
Occupation
Service Electrician 2020 NEC
(revised wording of OP)
For the application of 230.2 can a separate service be installed if there is only a 2 hr wall between occupancies ??
Sounds like something a fire alarm contractor, or plan checker can help with.
 

Joe.B

Senior Member
Location
Myrtletown Ca
Occupation
Building Inspector
It's going to depend on what the occupancies are. In order to use a wall to "create" two buildings it must be a "fire wall" constructed per 706. Not a "fire barrier" (707) or "fire partition" (708).
706.4.jpg
You also need to look at 508.
508.4.jpg
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Thanks guys...
In my old age I am amazed at how many inspectors enforce "rules" that are based on habits and hearsay and not knowledge.
Locally I have heard for years that in order for a stricture to be considered multiple buildings a 4 hour wall was required,
 

Joe.B

Senior Member
Location
Myrtletown Ca
Occupation
Building Inspector
Locally I have heard for years that in order for a stricture to be considered multiple buildings a 4 hour wall was required,
There's a lot of that. It makes sense though, a 4-hour wall will work anywhere, no need to figure out what the occupancies are.
 

hillbilly1

Senior Member
Location
North Georgia mountains
Occupation
Owner/electrical contractor
Usually a block wall is considered a four hour rating, and extend above the roof line. I can’t remember if 8” block or 16” block must be used, but I think it is 8”. A 2 hr wall usually just goes to the deck.
 