Thank you for this document. Seems like there does not have to be a firewall inside shipping containers converted to battery storage units.
Yes there is likely no specific requirement for a firewall in that situation. However there is likely a requirement for large scale fire testing (UL9450A) and fire department review and approval for such an installation. Unless you're state is behind on adopting the latest ICC or NFPA code related to this.
The 2024 IFC section on energy storage systems can be found here.
There is a table for threshold capacities for when that code applies, depending on technology. For example for lithium ion batteries it is 20kWh. (For residential installations the resi code may apply instead, but I gather that's not what you're dealing with.)
Not that I know if your jurisdiction has adopted the 2024 IFC.