rickysib

Member
We are dealing with a 4 hour CMU firewall construction. Other than fire sealing/flame stopping does the UL or NEC speak to any restrictions on electrical penetrations or conduits run in the firewall? We are going through final inspections and the fire marshall is now questioning it...
thanks
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
You will need to look into your local building codes and then the UL Orange Books, AKA, Fire Resistive Directory.

You can go to the UL web site but it is not very easy to use.

Roger
 

rickysib

Member
rickysib said:
We are dealing with a 4 hour CMU firewall construction. Other than fire sealing/flame stopping does the UL or NEC speak to any restrictions on electrical penetrations or conduits run in the firewall? We are going through final inspections and the fire marshall is now questioning it...
thanks
Thanks, yes we have consulted the UL books, but there isn't anything there that prevents it. Not sure where this guy is coming from. Again, thanks for your confirmation.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
UL has to do with product ratings, not installations (except indirectly in that a UL listed product must be correctly installed). The UBC and NFPA Code are what dictates the requirements at the installation and IIRC, does address firewall penetrations of conduit. This presentation outlines it well, specifically page 14 addresses your issue.

http://www.thomasjdonnellyinc.com/statementofconditions.ppt

So essentially, if your conduit has a fire rating equal to or greater than the fire wall it penetrates, then all you need to do is seal the edges with an approved material.
 

charlie

Senior Member
Location
Indianapolis
rickysib said:
. . . 4 hour CMU firewall construction. . .
As far as I know, CMU (concrete masonry units) construction needs only grout or intumescent material for the penetrations. I have never heard of the need for internal blocking or fire stopping of the conduit runs. :smile:
 

sandsnow

Senior Member
The fire resistive rating of the wall is only part of the story.

You have to consider what the wall is being used for. A good example is a Vertical Exit Enclosure, better known as a stairwell. In a High Rise bldg these are two hour fire resistive construction.

The rest of the story is that penetrations through these wall are NOT permitted unless the item serves the stairwell. Such as electrical for lighting or fire sprinklers.
 