just curious why do you not bond the neutral and ground in a meter socket with no breaker. You can't over ground something. What could go wrong
but what if it is just a meter can with no disconnect.you dont bond the neutral and ground there.Almost all meter sockets have the neutral bonded directly to the enclosure. On the line side of the service disconnect all metal parts are connected to the neutral.
but what if it is just a meter can with no disconnect.you dont bond the neutral and ground there.
There is no EGC on the supply side of the main bonding jumper - which will be at the service disconnecting means.but what if it is just a meter can with no disconnect.you dont bond the neutral and ground there.