GlennG
Member
- Location
- Hicksville, NY
I just got my first pool job and there are a few things that are confusing me since i started reading up. Its a 4 foot above ground pool with a pump only, no filter, so i am under the impression it is considered a permanent installation because its greater than 42''. If that stands true than as far as i know I will need my equipotential bonding ring around the pool 4-6'' deep and bonding lug on 4 points, and then 6 feet from the edge of pool i will have a switch, time clock and twist-lock receptacle all GFCI protected. Also the General purpose GFCI between 6-20 feet from edge. My three main questions are
1- can the general purpose GFCI be on the same post as the twistlock ?
2- Does the equipotential bond wire terminate on the ground lug on the pump and connect back to the egc through the cord?
3- Can the timeclock act as a disconnect switch for the pump?
I would appreciate thoughts, i want to make sure i am on the right page and not overlooking anything or doing something necessary. thanks
1- can the general purpose GFCI be on the same post as the twistlock ?
2- Does the equipotential bond wire terminate on the ground lug on the pump and connect back to the egc through the cord?
3- Can the timeclock act as a disconnect switch for the pump?
I would appreciate thoughts, i want to make sure i am on the right page and not overlooking anything or doing something necessary. thanks