Hi all,
Today I eliminated power to an original sub panel in a garage to relocate it and I pulled out the sub feed conductors that were feeding it from the meter/main/load center service panel. The main service panel also feeds other loads including another small sub panel upstairs that was added during a previous remodel that was before my time out there and is completely separately fed from the original sub panel that I was dealing with in the garage.
After taking out the branch circuit breakers and disconnecting the branch circuit neutrals from the garage sub panel, I got shocked (and was very shocked to actually receive a shock!). After some preliminary investigation, I discovered that when turning on ONE single pole circuit breaker in the upstairs sub panel, that in turn 120V energizes four different individual branch circuit conductors in the garage sub panel. One conductor that becomes energized is a white conductor which was originally landed on the neutral bus and has two associated hots (black and red) going out in the same conduit. There is also another conduit with a black, red, white, and all three of these conductors are energized at 120V individually to ground when the same circuit breaker is turned on in the upstairs sub panel.
Now I know that I'm looking for a connection or connections that are not suppose to have been connected, but any feedback or previous experience on such a situation would be very much appreciated.
Today I eliminated power to an original sub panel in a garage to relocate it and I pulled out the sub feed conductors that were feeding it from the meter/main/load center service panel. The main service panel also feeds other loads including another small sub panel upstairs that was added during a previous remodel that was before my time out there and is completely separately fed from the original sub panel that I was dealing with in the garage.
After taking out the branch circuit breakers and disconnecting the branch circuit neutrals from the garage sub panel, I got shocked (and was very shocked to actually receive a shock!). After some preliminary investigation, I discovered that when turning on ONE single pole circuit breaker in the upstairs sub panel, that in turn 120V energizes four different individual branch circuit conductors in the garage sub panel. One conductor that becomes energized is a white conductor which was originally landed on the neutral bus and has two associated hots (black and red) going out in the same conduit. There is also another conduit with a black, red, white, and all three of these conductors are energized at 120V individually to ground when the same circuit breaker is turned on in the upstairs sub panel.
Now I know that I'm looking for a connection or connections that are not suppose to have been connected, but any feedback or previous experience on such a situation would be very much appreciated.