First time on Class 1 system

Status
Not open for further replies.

joeyww12000

Senior Member
Location
Chatsworth GA
I am helping install door lock control wiring in a jail. The conductors are Class 1,#14 and #18 stranded. How do I go about conduit fill for these types of conductors? The doors are controlled by PLC's and are 24v I think. Im just wondering how to go about fill since 360 of these conductors were put in a 3 inch conduit. They fit, but was it correct to do so? Just doesnt seem kosher to me. Nobody else seemed to care about finding out if they could do this and just did it. I want to know the correct way and how to calculate this. Thanks.
 
Joey,

BPH is correct, however I know you are learning and you like to know details.

As soon as you know you're dealing with lv wiring look at Art. 725. In your case Class 1, look specifically at 725.3(A). This refers you to 300.17. Read the paragraph and then look at the FPN. Assuming they used EMT, look at 358.22 which directs you to Table 1, Chapter 9. This directs you to Annex C, Table C.1 for EMT. Look at THHN, 14 gauge wires, max. allowed in 3" is 364.

See how easy that was...LOL.

If you were asked this on a test though it would be a very complicated calculation.
 
Having worked on these types of systems, I would strongly recommend that you look at quick pull or similar products from other suppliers. The bundles are custom as to wire size and color. When I did this kind of work we would use a bundle where wire colors matched the pigtails on the door locks and position switches. While buying the conductor this way costs about twice as much as buying single conductors, you more than make that up in reduced labor.
 
So you dont have to worry about derating or anything? You just go by the chart for number of conductors that can legally go in a 3" conduit?
It is my opinion that Exception 1 to 310.15(B)(2) applies and derating is not required for control conductors.
 