W wireday Senior Member Location New England Occupation Master electrician Jul 5, 2017 #1 Is it permitted to fish wire down walls and over ceilings in finished buildings without support ? They may not be 1 1/4 away from edge etc.
Is it permitted to fish wire down walls and over ceilings in finished buildings without support ? They may not be 1 1/4 away from edge etc.
W wireday Senior Member Location New England Occupation Master electrician Jul 5, 2017 #2 Looks like 300.4 (D) exception 2 applies.
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Jul 5, 2017 #3 Yes, if the wall is already finished there is less of a likelihood of the cable being damaged.
480sparky Senior Member Location Iowegia Jul 5, 2017 #4 I'd really like to see someone fish wires in a stud cavity and maintain 1¼" clearance from the wall.