fixed electrical equipment

Status
Not open for further replies.

copper chopper

Senior Member
Location
wisconsin
517.13 Grounding of Receptacles and Fixed Electrical
Equipment in Patient Care Areas.
The application is this- in a patient care room there is an undercabinet light, this light is on a normal circuit and wired with regular (blue colored) mc cable which does not satisfy this article. In my eyes I say that the light is a fixed piece of electrical equipment and has to be wired with HCI or (green) MC cable. Since the code has no definition of fixed piece of equipment I still say it is. WHAT DO YOU THINK?????
 
I would say the lighting is fixed and art. 517.13(A) states that all branch circuits serving patient care areas shall be provided with an effective ground fault....So I am curious why the header just says receptacles and fixed equip.
 