I’m looking into installing a 15kw residential heater. It requires a 60 and 30 amp circuit.
I know standard practice is to pull a 6-2 nm conductor and a 10-2nm conductor.
But I noticed the min circuit amps is 55 and max ocpd is 60
Nec require this to be continuous load calculations on conductors with increases amps to 68.75. Which would rule out the 6-2nm
how do people get away with using a 6-2 and not a 4-2? Thx