i have a fluorescent light with a cord and plug attached to it. can you cut off plug and hard wire fixture using the same cord attached? or is that a code violation? do you have to use specific cord?
 

Sierrasparky

Senior Member
Location
USA
Occupation
Electrician ,contractor
I would say not listed for that.
However who is going to know if you install just like any other pendant type mount.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
There may well be exceptions but all the Fluorescent fixtures I have inspected that have a factory cord allowing compliance with 410.62(C) employ a cord that can be distinguished from a Type SJO or similar cord in that they have a more durable insulation.
 

John120/240

Senior Member
Location
Olathe, Kansas
i have a fluorescent light with a cord and plug attached to it. can you cut off plug and hard wire fixture using the same cord attached? or is that a code violation? do you have to use specific cord?

Yes cutting the cord cap off is a violation, but I may know someone who cut the cord cap off & never lost a wink of sleep.
 