Fixture Driver
Alwayslearningelec
NJ
Estimator
I pulled up spec sheet for fixture I'm estimating. Does below mean it's one or the other?(0-10v or 120/277v). Need to know if I need to bring dimming wires to it.
BTW the controls/switches are not specified so I can't even get clued in by that.
0-10 volt dimming is 0-10 volt dimming.
This luminaire can operate at 120 or 277 supply volts, and likely anything in between?
The 1% is maybe minimum dimmed lighting output ability?
I agree that this is the most likely interpretation of the 1% spec. Some LED drivers will turn off the output when the 0-10V control is below some value, typically somewhere between 0.5 and 1.0VDC (aka "dim to off').
The driver, and probably the dimmer, receive unswitched power.
The 0-10v wire pair communicate between the two for dimming.
You don't have to use the dimming feature if you don't need it.
Or you can get dimming or non-dimming line-voltage drivers.