I think your talking lay in flourescents. Attached to the grid is probably a manufactor spec.
If independent tie wires are used the NEC requires them to be marked as different from the cieling tie wires.
I am pretty sure that tieing them independently is a building code in certain parts of the country.
I have read this also. Doesn't is say the fixtures must be supported to the framing member (framing member must be attached to building structure). The fixture itself is not required per NEC to be independently supported from the building structure. If you have a large project with a lot of fixtures, providing independent supports can be expensive if not required. This is why I brought up the question.
Also the grid manufactuer would have to state that that the grid would support all the extra weight, I doubt they will.
Interestingly, while I've added support wires for cabling, I never have had to for lay-ins.Every jurisdiction I have worked in-VA, NC, MD, CA- has required at least two independent wires on a diagonal support for lay in fixtures and such.
Every Armstrong (are there any others?)Grid System I have ever checked on listed fixture weight capacities between 40 and 70 lbs depending on grid layout.
They go on to say fixtures weighing more than 56 lbs should be independently supported. I'll venture a guess that most, if not all, 2x4 lay-ins weigh less than 56 lbs.
See page 4 of this document.
http://www.armstrong.com/common/c2002/content/files/8388.pdf
Interestingly, while I've added support wires for cabling, I never have had to for lay-ins.
Here we are required to independently support the fixtures but it is an IBC requirement not a NEC requirement.