on a electrical installation i had a inspector accept my m/c cable daisy chained fixture to fixture,that was rough in. then on final he said i could not use the fixture as a raceway, the fixturesare 2x4 toffer lay ins and are ul rated. i changed them. who is right
 
I agree, what you did is certainly not using the fixture as a raceway. This is a very common installation technique. How did he want you to install them?
 
Craig,

How did you daisey-chain them together, was it from the factory junction

plate on the top of the fixture, or did you come in one end of the fixture and

out the other???
 
benaround said:
Craig,

How did you daisey-chain them together, was it from the factory junction

plate on the top of the fixture, or did you come in one end of the fixture and

out the other???


Should it matter?
 
Why would he, and how could he? I would have asked/fought this one before changing it. Frankly, I am sick and tired of Inspectors who attempt to enforce non-existant codes from faulty memories of what they might have thought it said, and call it gospel. Without siting a code or other reason... Sometimes it is nessesary to advocate for yourself and your customer against these types, and pull out a book and make them find it. Granted what it says is subject to THEIR interpetation, but they have a harder time pulling it out of their wazzoo if it is just not there, and you get the opprotunity to either learn or debate if it is.

410.31, and 410.32 cover this situation, (as raceways) but 'georgestolz' nailed right off - they were not used as raceways, they were used as 'junction boxes' with feed 'through wiring'... 410.10 & 410.11 And odds are that the fixture described is rated/listed for all of the above situations. (Other types my not be, but very doubtful in a 2X4 troffer.)
 