flightline
I would like your opinion on a matter that has recently come up. The situation is a custom home in our town, but this situation could be found most anywhere. In this instance, there are a number of brick columns that hold up a rear deck and extend upward a few more feet. These columns are topped with a smooth limestone cap. In these columns, the electrical contractor has stubbed up at least one, if not two ?? EMT?s with 2 conductors each in them, [no equipment grounding conductor; he?s using the EMT itself as the equipment grounding means as permitted by 250].
Herein lies the problem. The contractor did not install a box at each fixture location. As I interpret 300.15, this is a violation. You should know that these are coach style fixtures with bottom mounting canopy that would appear to be set up for mounting to a box. My discussion centered around 300.15 for these style fixtures, plus questioned how equipment grounding would be accomplished and maintained. Another concern is current leakage should the fixture canopies become watterlogged from the rain or snow, and the installation having no positive equipment ground. The contractor's response is " that's the way we always do it". Another aside, the general contractor did not have the brick pillars complete when we did rough inspection. Our next opportunity to see this project is at final. To pass final, all fixtures must be in place, with all lamps in place, working, and caulked to the exterior finish to maintain weathertight seal. There is no opportunity to inspect these without dismantling the work already done. Yet, the electrical contractor admitted that there was no box; he simply just wire nutted the connections below the canopy, and fastened the fixtures to the limestone cap with some sort of concrete anchor.
The permissive voice of the NEC in 410.16(A) says:
410.16 Means of Support.
(A) Outlet Boxes. Outlet boxes or fittings installed as required by 314.23 shall be permitted to support luminaries (fixtures).
The NEC Handbook goes on further to say:
Regardless of whether a luminaire is attached to an outlet box or is supported independently of the outlet box, care should be taken to securely fasten the outlet box or support the independent rod or hanger in order to ensure that the luminaire is securely mounted in place. The luminaire may be securely mounted to the box; however, if the box is not secured, it becomes the weak link in the luminaire support.
314.27 Outlet Boxes.
(A) Boxes at Luminaire (Lighting Fixture) Outlets.
Boxes used at luminaire (lighting fixture) or lampholder outlets shall be designed for the purpose. At every outlet used exclusively for lighting, the box shall be designed or installed so that a luminaire (lighting fixture) may be
attached.
It is the contractor?s contention that since the code section is permissive and says shall be ?permitted? that it is not mandatory. It is my position that 300.15 supercedes the 410.16 verbiage.
300.15 Boxes, Conduit Bodies, or Fittings?Where Required.
A box shall be installed at each outlet and switch point for concealed knob-and-tube wiring.
Fittings and connectors shall be used only with the specific wiring methods for which they are designed and listed. Where the wiring method is conduit, tubing, Type AC cable, Type MC cable, Type MI cable, nonmetallic-sheathed
cable, or other cables, a box or conduit body complying with Article 314 shall be installed at each conductor splice point, outlet point, switch point, junction point, termination point, or pull point, unless otherwise permitted in 300.15(A)
through (M).
Thanks for your answers.
attached.
through (M).