If we have a HVAC unit that has (9) 5HP fan motors, the calculations for this would be:
FLA: 68.4
MCA: 70.3
MOP: 77.9 or a 70A Breaker.
Now the MOP can't be less than the MCA in this case as it would probably cause nuisance trips. If we make it an 80A breaker, that seems reasonable, but what about 80% breaker rating? Would have to be a 90A breaker to be less than the 80% (72A).