Is it correct for a manufacturer to use the actual measured FLA of a machine, or do they have to use the summation of all the rated loads that could be on at the same time. The rated loads approach sounds straight forward enough, but does not always give the accurate representation of the machine FLA.
For Example:
I have a machine that has refrigeration compressors, nichrome wire heaters, immersion boiler heaters, and an air circulator fan. All of these load could be on simultaneously, but not at their full rated load. For example, the compressor can draw 15A at rated load, but with the heaters on 100% they would be drawing less than the 15A because although they are on, they are not under any load. The compressors eventual time out and will shut completely off, but for a brief period of time (approximately 1 minute) they will be on simultaneously with the heaters.
For a situation like this, am I able to physically measure what the full load amps are for the machine, which will appear on the nameplate, and also use that to size my equipment OCPD?
For Example:
I have a machine that has refrigeration compressors, nichrome wire heaters, immersion boiler heaters, and an air circulator fan. All of these load could be on simultaneously, but not at their full rated load. For example, the compressor can draw 15A at rated load, but with the heaters on 100% they would be drawing less than the 15A because although they are on, they are not under any load. The compressors eventual time out and will shut completely off, but for a brief period of time (approximately 1 minute) they will be on simultaneously with the heaters.
For a situation like this, am I able to physically measure what the full load amps are for the machine, which will appear on the nameplate, and also use that to size my equipment OCPD?