flashlight
Senior Member
- Location
- NY, NY
- Occupation
- Electrician, semi-retired
We just got a violation for an installation feeding 2 panels from one switch with double lugs. The switch was part of the service equipment.
The disconnect is fused at 150A and the main panel it feeds is 80 feet away and 150A also. The smaller panel is much closer (5 feet) and fed by #6's protected at end of run by 2P 60A CB w/ tie down.
Inspector says conductors for 2nd panel are a tap (which is true I think)
and no taps allowed in service switch. He wants us to put a gutter next
to switch and tap there.
He did not give us code section. Is he correct ?
Thanks !
The disconnect is fused at 150A and the main panel it feeds is 80 feet away and 150A also. The smaller panel is much closer (5 feet) and fed by #6's protected at end of run by 2P 60A CB w/ tie down.
Inspector says conductors for 2nd panel are a tap (which is true I think)
and no taps allowed in service switch. He wants us to put a gutter next
to switch and tap there.
He did not give us code section. Is he correct ?
Thanks !