Thanks so much for the reply, this is interesting stuff.
rbalex said:
The flammability range is very broad ? from 2.5 to 97%. The significance is that, depending on the leakage mechanism, while the area would indeed be toxic it could also rapidly enter the flammability range such that portable items could still ignite the area.
This is true, and I am not arguing this point, but consider this as well: Hydrazine fuels will react with carbon dioxide and oxygen in the air. MMH may ignite spontaneously when exposed to materials with large surface areas or when it comes in contact with metal oxides such as rust. So if it needs nothing but rust or air to ignite it, our equipment sparking isn't going to make much of a difference. Since the lower flammable limit of 2.5% concentration of MMH equals 25,000 parts per million and MMH is IDLH at only 20 ppm, it would be a bad, bad day if MMH existed in concentrations that were flammable in our facility.
I realize that portable equipment is not really covered by the NEC, but OSHA does state in one of their Standard Interpretation letters that these items shall not be used in Classified areas unless approved for that area.
Yes, MMH is a nasty commodity, and we do have many controls in place. It is in a system contained in a "vehicle" with many redundant valves, etc. to contain it and is only present in our area when that vehicle is being processed. Flammable concentrations should not exist in our area unless there is a catastrophic failure, except during certain operations that are performed only infrequently involving self contained atmospheric pressure ensembles for workers- a full rubber suit with its own air supply. Before these operations the area is walked down by the fire marshall and several safety representatives and engineers to ensure that it is safe for hazardous operations. In all actuality, even during these operations there would have to be a major failure before MMH would be present in ignitable concentrations, but some vapors are expected. Toxic vapor checks are performed throughout the task. Our processes/equipment have not changed for the last 25 years or so, but all of a sudden we find ourselves working in a classified area. We are not sure why we are now classified and how everything works, hence my question.
Here is another one for you, If our "vehicle" containing the flammable liquid is no longer present, then do the rules of the classification apply? We have been told that they do not, but reading this forum I am not so sure.
Thanks for the info!