tomstollmeyer
Member
- Location
- San Luis Obispo, CA
I have an installation, at a fire station, where a building, classified as "flammable storage", is located within 20' of an above ground fuel dispensing tank & unit.
As per the drawings a weather proof light switch is shown to be mounted at +48" outside of the entrance door to the flammable storage. (within 20' of the fuel dispenser). Additionally the routing of the conduit for the light switch is shown surface mounted on the inside of this building, using eys seal offs and Class1, Division 2 rated fittings and conduit.
Additionally, there is also a light pole with a 24" above ground concrete pole base, also located within the 20' perimeter of the fuel dispenser.
Question 1: Does the light switch mounted on the flammable storage building installed at +48" need to be Class 1, Division 1? Or is the weather proof switch allowed?
Question 2: Does the conduit routed inside the building for the light switch need to be Class 1, Division 2? Would this also apply to the light fixture installed on the ceiling (approx 8').
Question 3: The light pole has a splice located in the light pole which is about 36" above finish grade. Is this allowed?
I have written several RFI's, to the state, regarding all of the above. Only to get a response to install as per drawings. I have reviewed Art 500 and I am unable to come up with definative answers. I have always been under the assumption that nothing is allowed within the 20' perimeter of fuel dispensing, unless it complies with Class 1, Division 1 standards.
As per the drawings a weather proof light switch is shown to be mounted at +48" outside of the entrance door to the flammable storage. (within 20' of the fuel dispenser). Additionally the routing of the conduit for the light switch is shown surface mounted on the inside of this building, using eys seal offs and Class1, Division 2 rated fittings and conduit.
Additionally, there is also a light pole with a 24" above ground concrete pole base, also located within the 20' perimeter of the fuel dispenser.
Question 1: Does the light switch mounted on the flammable storage building installed at +48" need to be Class 1, Division 1? Or is the weather proof switch allowed?
Question 2: Does the conduit routed inside the building for the light switch need to be Class 1, Division 2? Would this also apply to the light fixture installed on the ceiling (approx 8').
Question 3: The light pole has a splice located in the light pole which is about 36" above finish grade. Is this allowed?
I have written several RFI's, to the state, regarding all of the above. Only to get a response to install as per drawings. I have reviewed Art 500 and I am unable to come up with definative answers. I have always been under the assumption that nothing is allowed within the 20' perimeter of fuel dispensing, unless it complies with Class 1, Division 1 standards.