Is the Reliance PR30 or PB30 suitable for use without an in use type cover? We are on the 2017 NEC.
Thanks
Bob
Thanks
Bob
I Spoke with my inspector, and he requires the device to be weatherproof while in use per 406.9(B)2(a)
Makes sense, but surprising how many locations (cities) these could not be installed in.
I went with a GE T030N instead, and looks like a nice unit.
Thanks,
Bob
I agree.A receptacle and an inlet are not the same. IMO there is no NEC requirement for the inlet to be used with the same in-use cover restriction as a receptacle. Inlets fall under 406.7.