FLC for 800 Hp 460VAC Motor

Status
Not open for further replies.

texasmike

Member
How (or where) do I get a FLC number for a 460 VAC motor larger than the 500 Hp entry in NEC table 430.250? The specific motor in question is 800 Hp, FLA = 917 amps, service factor 1.0.
Thanks.

texasmike
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
While the 1.2 is a good rule of thumb, what code section actually addresses the current for motors larger than 500 hp?. 430.6 addresses some cases outside the table values, but does not address motors larger than 500 hp.
 

Ingenieur

Senior Member
Location
Earth
If the code does not define it I would back calculate off the 500 hp
Fla = 590

i = (746 x hp) / (1.732 x eff x pf x 460)
solve for eff x pf call it k
k = (746 x 500) / (1.732 x 590 x 460) = 0.794

for 800 hp
i = (746 x 800) / (1.732 x 0.794 x 460) = 944 A

short version
800/500 x 590 = 944
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
It's not addressed in the NEC anywhere that I am aware of. As a generality, AHJs that I have encountered use the following statement out of 430.6.A.1 as justification for going ahead and using nameplate values:
Motors built for low speeds (less than
1200 RPM) or high torques may have higher full-load currents,
and multispeed motors will have full-load current
varying with speed, in which case the nameplate current
ratings shall be used.

But that doesn't help when you have to design the circuit and components long before the motor arrives and often before the motor is even ordered. The 1.2A/HP comes from an EASA (Electrical Apparatus Service Assoc.) guidebook I still have that has a reproduction of the 1996 NEC Table 430.150 (which is now 250) and at the bottom of that chart, there is one more row of values entitled "Over 200HP" and labeled;

[Approximate Amps / HP] [200V = 2.72] [208V = 2.64] [230V = 2.4] [460V = 1.2] [575V = .96] [2300V = .24] [4000V = .14]

I don't know if that is actually printed in the 1996 NEC, I no longer have a copy that old (it's not in the 2002 however). But even if it was, it no longer is. I have found that just like the values in 430.250, the number comes out a little conservatively higher than what I see on motors, so for sure don't use that for setting OL relays. But I find it's a good value to use for sizing conductors, OCPDs etc.
 

Ingenieur

Senior Member
Location
Earth
You can extrapolate off the table
seems fairly linear

200 hp = 240 A
assume 400 hp = 2 x 240 = 480 A
From table 400 hp = 477 A
0.6% lower

250 hp = 302
2 x 302 = 604 A
table 500 hp = 590 A
2% lower

and so on
most are ~2-3% lower than table values

400 hp = 477 A
2 x 477 = 954 A
my calc 944 A
my calc is 1% lower than 2 x 400 hp fla

944/800 = 1.18 A/hp
 

Besoeker

Senior Member
Location
UK
Took a picture of it...
I think the table is a good guide, perhaps a very good guide. But it has to based on assumptions about power factor and efficiency.
There has been a push for higher efficiencies in recent years so IE1 is standard, IE2 is high efficiency, and IE3 is premium. Not sure that the same table would apply to all.

FWIW, my stab at the 800HP (~600kW) made it 960A.
 
Last edited by a moderator:

Sahib

Senior Member
Location
India
There's a difference?
The 960A from my calculation is full load current.
But you can call it what you want.....................:p
Yes. NEC assigns motor full load current FLC which may not be same as motor name plate current FLA.
 
Last edited by a moderator:

Besoeker

Senior Member
Location
UK
But only up to 500HP. So the distinction becomes moot for this discussion.
I think that's a reply to Sahib's comment. I screwed up the quotation brackets.
It wouldn't be a distinction for me you see. I don't think we use FLA, just FLC.
 