Have customer wanting flex conduit(did not describe type yet) run underground for temporary application. About 500'. It's going to contain fiber cables. Should flex be run underground even if it only has fiber and is temporary? Thanks
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
You would need to use a fiber that was listed for direct burial since the FMC is just a sleeve. Not sure why you would use FMC it seems like a dumb choice when you could something like an armored direct burial cable.
 

SceneryDriver

Senior Member
Location
NJ
Occupation
Electrical and Automation Designer
IMO that would be the best choice. Direct burial innerduct typically bright orange so it's highly visible. Also it's smooth so pulling the fiber through it shouldn't be a problem. Pulling fiber through 500' of FMC might not be that easy.
This is the best choice. I have pulled through buried LFNC and it sucks, even when using wire lube. I mentioned that you can bury Liquidtite - I never said it was a good idea 😆


SceneryDriver
 

kwired

Electron manager
Location
NE Nebraska
I hate LFMC with a passion. I mean could they have chosen a material with a higher coefficient of friction???
If you stretch it really tight and straight it isn't nearly as bad.

ENT is same way. With corrugated interior some say it should pull easier than rigid PVC because of less surface contact - probably true but only if you get it really straight
 