Re: flex conduit
Infantryldr, if the FMC is longer than 6' in any size it will need one EGC. It doesn't matter what it is connecting to.
Below is a graphic and accompanying commentary form Mike Holts Training material.
Part VI. Equipment Grounding (Bonding) and Equipment Grounding (Bonding) Conductors
New text specifies when an equipment (bonding) conductor is required for flexible metal conduit and liquidtight flexible metal conduit.
(5) Listed Flexible Metal Conduit meeting all of the following conditions [348.60]. Figure 250-29
a. The flexible metallic conduit terminates in fittings listed for grounding (bonding).
b. The circuit conductors are protected by overcurrent devices rated 20A or less.
c. The combined length of the flexible metal conduit used as an equipment grounding conductor in the same fault return path doesn?t exceed 6 ft. Figure 250-30
d. Where flexibility is necessary, an equipment grounding (bonding) conductor must be installed in accordance with 250.102(E) regardless of the circuit rating or the length of the flexible metal conduit.
(6) Listed Liquidtight Flexible Metal Conduit meeting all of the following conditions [350.60]. Figure 250-31
a. The liquidtight flexible metal conduit terminates in fittings listed for grounding (bonding).
b. For 3/8 through 1/2 in., the circuit conductors are protected by overcurrent devices rated 20A or less.
c. For 3/4 through 11/4 in., the circuit conductors are protected by overcurrent devices rated 60A or less.
d. The combined length of the liquidtight flexible metal conduit in the same ground return path doesn?t exceed 6 ft.
e. Where flexibility is necessary, an equipment grounding (bonding) conductor must be installed in accordance with 250.102(E) regardless of the circuit rating or the length of the flexible metal conduit.