Flex Connection To Motors or Vibrating Equip

Status
Not open for further replies.

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
Is it code to have a specific bushing(grounding etc.) when connecting steel or sealtite flex to a motor or xfrmr? Thanks.
 
If the flex is used for vibration then a wire type EGC is required.
I would recommend a plastic insulating bushing at the motor end, is required depending on wire size
 
No specific bushing is required unless there are concentric or eccentric KO's involved. I see bonding bushings on transformers every day but they are not required.
 