The site is a large IT room (data center)fully compliant with Art 645. From a Power Distribution Unit, each branch circuit cable is distributed under the 30" raised floor in flex LT metal conduit, terminating in a receptacle box as permitted by Art 645.5(D). The equipment to be plugged into the receptacle sits above it on the raised floor and comes equipped with a ten-foot cord.
QUESTION. Can I plug the cord into the receptacle without running it in conduit? It is not marked DP cable.
Art 400.8(2) seems to prohibit "where run through holes in... floors, (unless specifically permitted in 400.7). However, 400.7(A)6)permits use of flex cord "for connection of utilization equipment to facilitate frequent interchange," and 400.7(A)(9) permits Data Processing cables as permitted by 645.5. If I look there, I find "the data processing system shall be permitted to be connected to a branch circuit by any of the following means listed for the purpose:"
"(1) flex cord & attachment plug cap not to exceed 15 ft"
"(2) cord set assembly. Where run on the surface of the floor, they shall be protected against physical damage."
So it seems to me to be permitted as long as the cord is not laying on the surface of the floor and it is part of the listed IT equipment. But AHJ says no. Who's right?
QUESTION. Can I plug the cord into the receptacle without running it in conduit? It is not marked DP cable.
Art 400.8(2) seems to prohibit "where run through holes in... floors, (unless specifically permitted in 400.7). However, 400.7(A)6)permits use of flex cord "for connection of utilization equipment to facilitate frequent interchange," and 400.7(A)(9) permits Data Processing cables as permitted by 645.5. If I look there, I find "the data processing system shall be permitted to be connected to a branch circuit by any of the following means listed for the purpose:"
"(1) flex cord & attachment plug cap not to exceed 15 ft"
"(2) cord set assembly. Where run on the surface of the floor, they shall be protected against physical damage."
So it seems to me to be permitted as long as the cord is not laying on the surface of the floor and it is part of the listed IT equipment. But AHJ says no. Who's right?