gtrojas

Member
when using a factory flex cord for quick disconnect to a motor does the white wire need to be indentfy as hot conductor i believe 400 -7 say it does not please help me here
 

gtrojas

Member
Re: flex cords

no its a quick disc flex cord that iam providing
but the insperctor is saying i have to indentify
 

gregory

Senior Member
Re: flex cords

200.7 C(3) Where a flexible cord, having one conductor identified by a white or gray outer finish or three continuous white stripes or by any other means permitted by 400.22, is used for connecting an appliance or equipment permitted by 400.7. This shall apply to flexible cords connected to outlets whether or not the outlet is supplied by a circuit that has a grounded conductor.
FPN: The color gray may have been used in the past as an ungrounded conductor. Care should be taken when working on existing systems

According to the above article, you would not have to identify white conductor as a phase conductor.
 