Those short sections do not fall under the rules for CSST. Nec just states that the gas pipe needs bonding but it can be bonding with the equipment grounding conductor of the circuit that feeds the gas appliance.
That's not how you bond CSST. Consider that the appliance end(s) of the CSST is grounded via the EGC of the circuit(s) supplying it. A lightning strike nearby can energize the incoming gas line, creating voltage across, and thus current through the CSST, damaging it.The idea of needing a bonding conductor along the entire length of CSST tubing, only to connect to a unbonded FAC connector seems silly to me.
We have always done it as Larry stated. Can you imagine what you would have to do if there were 8-10 runs if we had to run a wire along the entire length of the csst.
All that does is create parallel paths. Whichever path is less impedance carries more current. With lightning that lesser impedance path isn't always as obvious as with regular AC voltage/current. On top of that with a fairly direct hit you have a lot of current and a lot of damage regardless, it is those nearby strikes that put transients into a facility that they are mostly concerned with for the added bonding.My understand is that the bonding jumper goes from one end of the csst to the other like this.View attachment 21270
So when lighting strikes the CSST will be fine but the FAC connection will blow up.