Flex Metal Conduit in Drywall-Gypsum Wall

Status
Not open for further replies.

vidividi12

Member
Location
San Marino
Occupation
Electrician
Hi,

I know that flexible metal conduit can be used for connection to lighting fixtures and vibrating motors. However, I want to use flexible metal conduit for device(receptacle-switch) boxes in drywall instead of EMT. Is there any restrictive item in NEC? I found that FMC is permitted to be used in exposed and concealed locations(348.10) but I want to be sure. Can I use FMC in drywall instead of EMT?
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Yes, generally speaking it can be used where EMT is used. Article 517 has some restrictions though.

Roger
 

powerpete69

Senior Member
Location
Northeast, Ohio
Occupation
Professional Electrical Engineer
348.12 lists the places you can not use it. I think you are good to go assuming you are not pouring gasoline, oil or venting explosive gases down your wall.

Skimmed thru the rest of section 348, looks like you will be installing FMC for your receptacle-switch boxes. Looks like you can use it in your ceiling as well for light fixtures and what not. Feel free to use on your basement cinder walls as well assuming they are not wet.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
A few restrictions on FMC if longer than 6' is cannot be used as an EGC. Also if longer than 6' it cannot be 3/8".
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
You will need to seal the membrane penetration with a proper assembly, 3M, Rectorseal, Hilti, and other manufacturers have online help with their products.

Roger
 
Status
Not open for further replies.
Top