In a new hospital project an under counter light in a patients room was added to the project prior to drywall installation and cabinet installation. This was roughed in to a nearby critical circuit with hospital grade MC. Now the question has been asked if this meets code requirements.
In reviewing 517.30(C)(3) there are several exceptions that allow for the use of MC on the critical branch. (d) allows it where necessary to connect to equipment. If you refer the NEC definition of equipment you will find that a light is considered equipment. So if the question is if the word ?equipment? can be used to refer to a light. The answer per NEC definition is yes.
That leaves the argument on the interpretation of the word necessary. This word in not defined in the NEC. So an argument would need to be developed to show why this is necessary to the installation. For example: Flexibility is needed to fish the raceway in the cabinet. Hard pipe would not allow for the installation of the cabinets. The final or exact location of the light or the cabinet has not been determined so flexibility is needed.
What are your thoughts? Do you think the use of MC is acceptable in this installation?
In reviewing 517.30(C)(3) there are several exceptions that allow for the use of MC on the critical branch. (d) allows it where necessary to connect to equipment. If you refer the NEC definition of equipment you will find that a light is considered equipment. So if the question is if the word ?equipment? can be used to refer to a light. The answer per NEC definition is yes.
That leaves the argument on the interpretation of the word necessary. This word in not defined in the NEC. So an argument would need to be developed to show why this is necessary to the installation. For example: Flexibility is needed to fish the raceway in the cabinet. Hard pipe would not allow for the installation of the cabinets. The final or exact location of the light or the cabinet has not been determined so flexibility is needed.
What are your thoughts? Do you think the use of MC is acceptable in this installation?