M Michael Hays New member Jan 31, 2011 #1 Is it acceptible to run a structural steel ground conductor in EMT then transistion to flex the last 5 ft. to the xfmr?
Is it acceptible to run a structural steel ground conductor in EMT then transistion to flex the last 5 ft. to the xfmr?
roger Moderator Staff member Location Fl Occupation Retired Electrician Jan 31, 2011 #2 Yes it is, but both ends of the raceway must be bonded to the conductor. Personally I would just run the EMT all the way. Roger
Yes it is, but both ends of the raceway must be bonded to the conductor. Personally I would just run the EMT all the way. Roger