I have been asked a perennial question. Can we put a receptacle above a suspended ceiling to plug in a condesnate pump.
Per NEC, 400.8 my pat answer is "no" not so much because of the receptacle but because of the intended use of a flexible cord up there.
I have heard from people who can't back it up, that this rule was some how relaxed and that now we can put receptacles above suspended ceilings. Is there any truth to this.
Does it matter if the space is a plenum or not? In this case, it is not a plenum.
Thanks,
Mike
Per NEC, 400.8 my pat answer is "no" not so much because of the receptacle but because of the intended use of a flexible cord up there.
I have heard from people who can't back it up, that this rule was some how relaxed and that now we can put receptacles above suspended ceilings. Is there any truth to this.
Does it matter if the space is a plenum or not? In this case, it is not a plenum.