Flexible conduit in c1d1 locations
Guyute
I had a building that was changed from a C1D2 location to a C1D1 location. The building currently has liquid tight mettalic flex running to some motors and other equipment. What kind of flexible conduit is available to run to this equipment now that it is a C1D1 location?
Thanks
rbalex
See Section 501.10(A)(2). Technically, there are no "flexible conduits." However, there are flexible fittings - they are exceptionally expensive.
This Section also refers to Section 501.140 for applications of "Flexible Cords." The approved applications are very limited though.
james_mcquade
We use explosion proof felxible conduit at some of the plants i work in.
i believe that crouse-hinds is the manufacturer. I will try tomorrow to get the manufacturer info.
regards,
james
don_resqcapt19
regards,
james
The link in post #2 is to the Crouse Hinds product, but the point is that it is not called "flexible conduit" by the manufacturer.
james_mcquade
Sorry it took so long in getting back to you.
Crouse Hinds.
i have some part numbers as a feference.
ECLK115 AND ECGJH118
Explosion Proof Conduit Flexible Coupling is what i found on several websites.
regards,
James