Flexible conduit thru vent duct ( Class 1 Div 2 location )

Status
Not open for further replies.

Davebones

Senior Member
Paint storage room 12' x 12' . They are installing a vent duct to the roof . The roof fan sits on the curb and has a Rating for class 1 div location . It has a sleeve down thru middle for electrical feed . Can flexible liquid type be ran into duct work and then up to fan on roof ?
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
As I understand your description, installing the LFMC per Art 350 is not prohibited. Your major issue will be grounding/bonding per Sections 501.30 and 250.102.
 