Both LFMC and LFNC are permitted "For direct burial where listed and marked for the purpose." See the respective articles for restrictions on use.
As long as the installation is compliant, what is there to recommend? What would you use otherwise... Rigid PVC?Do you recommend the installation also from the pull box to the inverter (solaredge) that are close (3 feets) in ground installation. I need enter the inverter with 1" conduit and probably flexible is easy, but I never use it inside pull boxes
As long as the installation is compliant, what is there to recommend? What would you use otherwise... Rigid PVC?
LFNC is simply a PVC that is flexible, similar to the insulation of THW (or the inner insulation of THHN/THWN) only much thicker, with an integral spiraled nylon reinforcing member. It's pretty tough stuff.