not a big deal... im gonna give in and change the cord. but for future reference, i gotta know. 38.7 A appliance fed from a 50A, 208V, single phase ckt... used 6awg as i was out of 8's. fed it from recep and i made a cord/plug assemnly with 8/3 soow. inspector is questioning this since art. 400 rates 8awg soow at 40 A. he is saying that the cord is not rated to handle the 38.7 X 125%. the unit itself says to supply it with #8awg conductors. what am i missing? this inspector is tough, but reasonable, and i enjoy having these conversations with him, so any insight would be appreciated...